using clipper pmac, when working it shown the below fault message.

 

PMAC TCP/IP

 

The vital circuit was reset by the remote side. Close all connections to PMAC including PMACServer then replug.

 

what's the problem and how to solve this ?

Link to comment
Share on other sites

  • Replies 1
  • Created
  • Last Reply

Top Posters In This Topic

Popular Days

Top Posters In This Topic

This message appears when serious communication error occurs due to following reasons

1. Unplug or other wire breaks

Sol: Make sure that all wires are good and connections are tidy. Also, you can eliminate any switch or hub issue by replacing the extra hardware by a single crossover cable.

2. Pmac is non-responsive due to watchdog tripping or excessive servo load

Sol: Check the status of watchdog LED (red) when problem occurs. Normal mode is OFF. Also, try to turn off PLCs and run your test again. You can achieve it by simply setting I5=0

 

I hope it helps

 

Farooq