I have a problem with M-var referencing on the CLIPPER board.
When I make a reference:
M500->X:$078000,17,1
all is OK, but when I want to point to 2 consecutive bits:
M500->X:$078000,17,2
I get compilation error 3 "Data error or unrecognized command"
But at the same time the reference:
M500->X:$078000,20,4
is OK as well.
There is no problem with reference to any bit-area in DPRAM:
M500->X:$060FE7,0,4
Where is my mistake?
Posts: 675
Threads: 50
Joined: Jun 2008
The following is a cut and paste from Turbo Software Reference Manual:
Quote:M{constant}->X/Y:{address}
Function: Short Word M-Variable Definition
Scope: Global
Syntax: M{constant}[..{constant}]->
X[:]{address},{offset}[,{width}[,{format}]]
M{constant}[..{constant}]->
Y[:]{address},{offset}[,{width}[,{format}]]
where:
• {constant} is an integer from 0 to 8191 representing the number of the M-variable;
• the optional second{constant} must be at least as great as the first {constant} -- it represents the number of the end of the range;
• {address} is an integer constant from $000000 to $FFFFFF (0 to 16,777,215 if specified in decimal).
• {offset} is an integer constant from 0 to 23, representing the starting (least significant) bit of the word to be used in the M-variables, or 24 to specify the use of all 24 bits;
• {width} (optional) is an integer constant from the set {1, 4, 8, 12, 16, 20, 24}, representing the number of bits from the word to be used in the M-variables; if {width} is not specified, a value of 1 is assumed;
• {format} (optional) is a letter from the set [U, S, D, C], specifying how Turbo PMAC is to interpret this value: (U=Unsigned integer, S=Signed integer, D=Binary-coded Decimal, C=Complementary binary-coded decimal); if {format} is not specified, U is assumed.
Sina Sattari
Hardware Engineering Manager
Delta Tau Data Systems, Inc.
Posts: 659
Threads: 0
Joined: Jun 2008
The limitation in the format that is tripping you up is explained further below in the description:
*******************************
Legal values for bit width and bit offset are inter-related. The table below shows the possible values of
{width}, and the corresponding legal values of {offset} for each setting of {width}.
{width} {offset}
1 0 -- 23
4 0,4,8,12,16,20
8 0,4,8,12,16
12 0,4,8,12
16 0,4,8
20 0,4
24 0
**********************
Two things to note: You cannot specify a width of 2 bits, and if you specify a width greater than 1 bit, the starting bit must be divisible by 4.