Thread Rating:
  • 0 Vote(s) - 0 Average
  • 1
  • 2
  • 3
  • 4
  • 5
EncLoss
#1
I am having issues with

Code:
Motor[0].pEncLoss = Gate1[4].Chan[0].EncLossN.a;

I think I am following exactly as described in the "Using ACC-24E2S with Power PMAC 2010-08.pdf" and "Power PMAC V1-3

Firmware Additions.pdf" documents. RP22 and RP24 are reversed on both boards correctly.

The system starts as

Code:
Motor[0].pEncLoss=0
Gate1[4].Chan[0].EncLossN.a=$b9e00040


If I execute the command above
I am left with

Code:
Motor[0].pEncLoss=???


What could be wrong?

This fails in the terminal and I had this command in a PLC which runs on startup and it created a ConfigLoadErr which took hours to find.
Reply
#2
Daves,

Sorry for the trouble you had to go through. Here is the settings you can use for encoder loss detection setup:

ACC-24E2x external XOR circuit for differential quadrature encoders
Code:
Motor[x].pEncLoss = Acc24E2x[i].Chan[j].EncLossN.a
Motor[x].EncLossBit = 13    // Encoder loss bit
Motor[x].EncLossLevel = 0

ACC-24E3 internal XOR circuit for differential quadrature encoders
Code:
Motor[x].pEncLoss = Acc24E3[i].Chan[j].LossStatus.a
Motor[x].EncLossBit = 28    // “Transparent” loss bit
Motor[x].EncLossLevel = 1

Acc-24E3 sum-of-squares circuit for analog sine encoders and resolvers
Code:
Motor[x].pEncLoss = Acc24E3[i].Chan[j].SosError.a
Motor[x].EncLossBit = 31    // Sum-of-squares error bit
Motor[x].EncLossLevel = 1

Acc-24E3 serial encoder transmission (time-out) error bit
Code:
Motor[x].pEncLoss = Acc24E3[i].Chan[j].SerialEncDataB.a
Motor[x].EncLossBit = 31    // Protocol-dependent
Motor[x].EncLossLevel = 1

Sina Sattari
Chief Engineer
Delta Tau Data Systems, Inc.
Reply
#3
Daves,

I have checked the Motor[0].pEncLoss=Gate1[4].Chan[0].EncLossN.a on my system and it works as expected. When I query back the Motor[0].pEncLoss, I get the following as result:

Motor[0].pEncLoss=Cid[2].PartData[0].a

This is expected since the loss data is accessed through the ID chip based upon the design on ACC-24E2X.

Would you be able to post what you actually get as response to Motor[x].pEncLoss query?
Sina Sattari
Chief Engineer
Delta Tau Data Systems, Inc.
Reply
#4
Daves,

I have checked the released version of the firmware (1.3.0.0 date Jan 27, 2011) and I can see the problem. We have already fixed this problem in the firmware. We should be having a release on both firmware and IDE during the next two weeks when this problem will be resolved.

The problem is that the firmware doesn't decode the address of Gate1[i].Chan[j].EncLossN data structure properly when queried and since the same query result is being used to generate the pp_save.cfg file, the setting "Motor[0].pEncLoss=???" was being saved and upon loading of the pp_save.cfg would cause a problem.

Regards,
Sina Sattari
Chief Engineer
Delta Tau Data Systems, Inc.
Reply
#5
This looks like it is working in the 1.4.0.27 Sep 15 2011 release. Thank you, Dave

(08-08-2011, 03:47 PM)Sina Wrote: Daves,

I have checked the released version of the firmware (1.3.0.0 date Jan 27, 2011) and I can see the problem. We have already fixed this problem in the firmware. We should be having a release on both firmware and IDE during the next two weeks when this problem will be resolved.

The problem is that the firmware doesn't decode the address of Gate1[i].Chan[j].EncLossN data structure properly when queried and since the same query result is being used to generate the pp_save.cfg file, the setting "Motor[0].pEncLoss=???" was being saved and upon loading of the pp_save.cfg would cause a problem.

Regards,

Reply
#6
Thanks Daves for checking on this.

Regards,
Sina Sattari
Chief Engineer
Delta Tau Data Systems, Inc.
Reply
#7
Dear all,

If i active the encloss function for a serial encoder on a PowerBrick directly in a plc at startup, i will trigger the EncLoss error.
I had to apply a timer of 8s to get ride of the error. Is it normal? Is there a status i can read instead of a timer, or a command i can send to speed up the startup?
The encoder configuration (Acc84B) is made before the enloss activation

Motor[1].EncLossBit=31
Motor[1].EncLossLevel=1
Motor[1].EncLossLimit=0
call timer.wait(8000);
Motor[1].pEncLoss=Acc84B[0].Chan[0].SerialencDataB.a

Thank you!