Why am I seeing weird card addresses?


Guest DavisG

Recommended Posts

Guest DavisG
Ok - you've got 3 i/o cards in your rack, but are seeing gates at gateio[0], [1], [5], [9], and [13] (or something equally odd). I've got a customer who had this situation - turns out they have a total of 9 UMAC racks, and on one of the racks one ACC-65E had all of the SW1 dip switches were backwards. I.E. OFF was set to ON and ON was set to OFF. Once the DIP was set correctly the problem disappeared.
Link to comment
Share on other sites