Im trying to understand the profile from a commanded move that I have issued.

In CS #1 I have a single motor setup as &1#1->2048X and using lookahead as "define lookahead 10000".

When I issues the online command "&1 cpx inc X+100000" notice the motor start moving with a negative velocity, after the motor reached aprox 20,000 counts the velocity reverses and willl continue to move until I issue &1a ( I have not waited until the move should have stopped ).

I have included the captured profile.

The only thing that I can think of is that the motion has started without first a pmatch to establish to current position of the axis.

Is there something else going on here ?

What must I do to simple have the axis move +100,00 user units ?

(the command was issued at about the 2 sec mark )

Reply
#2
You don't need the '+' symbol - I'm not sure what the effect would be (and don't want to try it on the machine on which I am working). The command:

cpx inc X100000

should work assuming that everything else is set up correctly
Reply
#3
(04-20-2011, 01:15 PM)DavisG Wrote: You don't need the '+' symbol - I'm not sure what the effect would be (and don't want to try it on the machine on which I am working). The command:

cpx inc X100000

should work assuming that everything else is set up correctly

Not using the "+" has no effect.
I have a little more information on how to create this.
1) #1hmz
2) #1J+ for > 50,000 counts
3) &1a
4) &1 cpx abs X1
5) &1a around 20,000 counts
6) &1 cpx inc X100000

This will cause the motor to move to about 10,000 counts and then reverse direction.

Even abs moves for everything will cause this. It also effects the acceleration for the moves. I think that issuing the "&1a" is messing up everything and not allowing a clean recovery.

Reply
#4
We have not been able to duplicate this here. Some questions:

What move mode are you in? Rapid? Linear?

Does this occur with no lookahead buffer defined?

Do you have a forward kinematic routine for the coordinate system?

Does the problem go away if you command "pmatch" before the move? (e.g. &1 cpx pmatch inc X100000)
Reply
#5
(04-21-2011, 11:54 AM)curtwilson Wrote: We have not been able to duplicate this here. Some questions:

What move mode are you in? Rapid? Linear?

Does this occur with no lookahead buffer defined?

Do you have a forward kinematic routine for the coordinate system?

Does the problem go away if you command "pmatch" before the move? (e.g. &1 cpx pmatch inc X100000)

I have included a snap shot of the CS status.

I do have a forward kinematic for the CS but I ony have #1->2048X defined in the CS, as shown in the Coord[1] Axis Definition

LookAhead is active

&1 cpx pmatch abs X10000 does exactly the same.

Thanks
John
Reply
#6
Is your forward kinematic routine a proper mathematical inverse of your axis definition?

If you eliminate the forward kinematic routine ("&1 open forward close") so that Power PMAC automatically inverts the axis definition equation to do the pmatch function, does the problem go away?
Reply
#7
(04-21-2011, 01:49 PM)curtwilson Wrote: Is your forward kinematic routine a proper mathematical inverse of your axis definition?

If you eliminate the forward kinematic routine ("&1 open forward close") so that Power PMAC automatically inverts the axis definition equation to do the pmatch function, does the problem go away?

I can't issues the command "&1 open forward close" from the terminal window, I get the following results:

Welcome to PowerPMAC terminal
Select device to start communication
SSH communication to PowerPMAC successful
Please wait!!! database Sync in progress
Database sync complete
&1
&1 open forward close
stdin:4:4: error #33: BUFFER IN USE: &1 open forward close
&1 open forward close
stdin:5:1: error #31: Buffer closed due to an error: &1 open forward close
p2801
P2801=2048
p2802
P2802=2048
#1->
&1#1->2048x
&1
list forward
C6=(L1-P2041)/P2801
C7=(L2-P2042)/P2802
list inverse
L1=(C6*P2801)+P2041
L2=(C7*P2802)+P2042
p2041
P2041=0
p2042
P2042=0
Reply
#8
John,

I just noticed a few things:

1. make sure you're not using &1p anywhere since it will call the forward kinematics routine and it won't allow you erasing it while it's being used. Then you should be able to use "&1 open forward close". Also, try deleting both forward and inverse kinematics. "&1 open inverse close"

2. In Power PMAC forward kinematics routine, you HAVE TO set KinAxisUsed or D0 to specify which axis are calculated using forward kinematics. If you don't then PMAC gets confused, since you have a definition for X axis both in kinematics and axis definition.

Sina Sattari
Hardware Engineering Manager
Delta Tau Data Systems, Inc.
Reply
#9
(04-21-2011, 04:57 PM)Sina Wrote: John,

I just noticed a few things:

1. make sure you're not using &1p anywhere since it will call the forward kinematics routine and it won't allow you erasing it while it's being used. Then you should be able to use "&1 open forward close". Also, try deleting both forward and inverse kinematics. "&1 open inverse close"

2. In Power PMAC forward kinematics routine, you HAVE TO set KinAxisUsed or D0 to specify which axis are calculated using forward kinematics. If you don't then PMAC gets confused, since you have a definition for X axis both in kinematics and axis definition.

Thanks for the info Sina,

I changed my kinematic file to clear both the forward and the inverse routines and downloaded the project
( as a side is there a way I can download a single file to the PPMAC ? )

The "&1 cpx inc X10000" now seems to be working correctly.

I will set them back and try your idea of setting D0 to 0

John
Reply
#10
(04-21-2011, 05:02 PM)JohnR Wrote:
(04-21-2011, 04:57 PM)Sina Wrote: John,

I just noticed a few things:

1. make sure you're not using &1p anywhere since it will call the forward kinematics routine and it won't allow you erasing it while it's being used. Then you should be able to use "&1 open forward close". Also, try deleting both forward and inverse kinematics. "&1 open inverse close"

2. In Power PMAC forward kinematics routine, you HAVE TO set KinAxisUsed or D0 to specify which axis are calculated using forward kinematics. If you don't then PMAC gets confused, since you have a definition for X axis both in kinematics and axis definition.

Thanks for the info Sina,

I changed my kinematic file to clear both the forward and the inverse routines and downloaded the project
( as a side is there a way I can download a single file to the PPMAC ? )

The "&1 cpx inc X10000" now seems to be working correctly.

I will set them back and try your idea of setting D0 to 0

John

Additional Info....

After disabling all of my PLCs I can now open then forward kinematic buffer.

If I set up the buffer such that "D0=0" is the only line in the buffer I still have my motion issue. If I delete all lines in the buffer the motoin works correctly.

Two thing going on I don't understand...

1) Why I can't open the buffer with the PLCs running ( I will attemp to narrow down exactly which PLC is the problem ).

2) Why does D0 = 0 cause my motoin issues ?

Thanks
John
Reply
#11
(04-21-2011, 05:56 PM)JohnR Wrote:
(04-21-2011, 05:02 PM)JohnR Wrote:
(04-21-2011, 04:57 PM)Sina Wrote: John,

I just noticed a few things:

1. make sure you're not using &1p anywhere since it will call the forward kinematics routine and it won't allow you erasing it while it's being used. Then you should be able to use "&1 open forward close". Also, try deleting both forward and inverse kinematics. "&1 open inverse close"

2. In Power PMAC forward kinematics routine, you HAVE TO set KinAxisUsed or D0 to specify which axis are calculated using forward kinematics. If you don't then PMAC gets confused, since you have a definition for X axis both in kinematics and axis definition.

Thanks for the info Sina,

I changed my kinematic file to clear both the forward and the inverse routines and downloaded the project
( as a side is there a way I can download a single file to the PPMAC ? )

The "&1 cpx inc X10000" now seems to be working correctly.

I will set them back and try your idea of setting D0 to 0

John

Additional Info....

After disabling all of my PLCs I can now open then forward kinematic buffer.

If I set up the buffer such that "D0=0" is the only line in the buffer I still have my motion issue. If I delete all lines in the buffer the motoin works correctly.

Two thing going on I don't understand...

1) Why I can't open the buffer with the PLCs running ( I will attemp to narrow down exactly which PLC is the problem ).

2) Why does D0 = 0 cause my motoin issues ?

Thanks
John

The following snippet from the terminal window shows PLC 8 is causing the open forward buffer problem...

open forward
D0=0
close
list forward
D0=0
enable plc 8
open forward
stdin:129:1: error #33: BUFFER IN USE: open forward
close
list plc 8
P1201=(Motor[1].ActPos-Motor[1].HomePos-Motor[1].MasterPos*((Motor[1].MacroCtrl&2)>>1))/(P2801)-P2041/P2801
P1202=(Motor[2].ActPos-Motor[2].HomePos-Motor[2].MasterPos*((Motor[2].MacroCtrl&2)>>1))/(P2802)-P2042/P2802
P1203=(Motor[3].ActPos-Motor[3].HomePos-Motor[3].MasterPos*((Motor[3].MacroCtrl&2)>>1))/(P2803)-P2043/P2803
P1204=(Motor[4].ActPos-Motor[4].HomePos-Motor[4].MasterPos*((Motor[4].MacroCtrl&2)>>1))/(P2804)-P2044/P2804
P1205=(Motor[5].ActPos-Motor[5].HomePos-Motor[5].MasterPos*((Motor[5].MacroCtrl&2)>>1))/(P2805)-P2045/P2805
P1206=(Motor[6].ActPos-Motor[6].HomePos-Motor[6].MasterPos*((Motor[6].MacroCtrl&2)>>1))/(P2806)-P2046/P2806
P1211=-sin(P1204)*cos(P1205)
P1212=cos(P1204)*cos(P1205)
P1213=sin(P1205)
P1214=P1201-sin(P1204)*(M291*cos(P1205)+M290)+M294*cos(P1204)
P1215=P1202+cos(P1204)*(M291*cos(P1205)+M290)+M294*sin(P1204)
P1216=P1203+M291*sin(P1205)
P2201=(Motor[9].ActPos-Motor[9].HomePos-Motor[9].MasterPos*((Motor[9].MacroCtrl&2)>>1))/(P2809)-P2049/P2809
P2202=(Motor[10].ActPos-Motor[10].HomePos-Motor[10].MasterPos*((Motor[10].MacroCtrl&2)>>1))/(P2810)-P2050/P2810
P2203=(Motor[11].ActPos-Motor[11].HomePos-Motor[11].MasterPos*((Motor[11].MacroCtrl&2)>>1))/(P2811)-P2051/P2811
P2204=(Motor[12].ActPos-Motor[12].HomePos-Motor[12].MasterPos*((Motor[12].MacroCtrl&2)>>1))/(P2812)-P2052/P2812
P2205=(Motor[13].ActPos-Motor[13].HomePos-Motor[13].MasterPos*((Motor[13].MacroCtrl&2)>>1))/(P2813)-P2053/P2813
P2206=(Motor[14].ActPos-Motor[14].HomePos-Motor[14].MasterPos*((Motor[14].MacroCtrl&2)>>1))/(P2814)-P2054/P2814
P2211=-sin(P2204)*cos(P2205)
P2212=cos(P2204)*cos(P2205)
P2213=sin(P2205)
P2214=P2201-sin(P2204)*(M293*cos(P2205)+M292)+M295*cos(P2204)
P2215=P2202+cos(P2204)*(M293*cos(P2205)+M292)+M295*sin(P2204)
P2216=P2203+M293*sin(P2205)

I don't see why this plc should be causing the buffer to be locked ?

John
Reply
#12
John:

D0 (for which the variable name macro is "KinAxisUsed") tells Power PMAC which axis positions you have computed in your forward kinematic routine. It will pick up the axis value(s) you have computed from the appropriate variable(s) and use them as the axis starting position(s) for the first move. By setting D0 to 0, you are telling Power PMAC not to pick up any positions, thus rendering your routine completely useless, so its intended "position matching" function is not performed, and the first move will used the wrong starting position. This looks like the source of your problem.

You need to set the appropriate bits of D0 to 1 for each axis in the coordinate system. For instance, if you have calculated X, Y, and Z positions, you should set bits 6, 7, and 8 to 1 for a value of $1C0.
Reply
#13
(04-22-2011, 09:44 AM)curtwilson Wrote: John:

D0 (for which the variable name macro is "KinAxisUsed") tells Power PMAC which axis positions you have computed in your forward kinematic routine. It will pick up the axis value(s) you have computed from the appropriate variable(s) and use them as the axis starting position(s) for the first move. By setting D0 to 0, you are telling Power PMAC not to pick up any positions, thus rendering your routine completely useless, so its intended "position matching" function is not performed, and the first move will used the wrong starting position. This looks like the source of your problem.

You need to set the appropriate bits of D0 to 1 for each axis in the coordinate system. For instance, if you have calculated X, Y, and Z positions, you should set bits 6, 7, and 8 to 1 for a value of $1C0.

Hi Curt,

I only am using a signle axis definition statement of
&1#1->2048X
I did not intend for the position matching to be done in the forward kinementic routine. I believed that setting D0 = 0 would instruct PPMAC to not assume any position calculation in to forward function and thus calculate all axis psotion from the inverse of the axis definition statement.

I agree that this looks like the cause of my motion problem. Why would a forward kinematic routine of D0=0 cause the profile to change ?

Thanks
John
Reply
#14
John:

If there is a forward kinematic routine for a coordinate system, Power PMAC will automatically use it for the position matching (pmatch) functionality that computes the starting axis position(s) from the motor positions. This is true even if the motors are assigned to axes with axis definition statements instead of being declared as inverse kinematic axes.

By setting the "KinAxisUsed" variable (D0) to 0, you are telling Power PMAC not to pick up any axis positions from the routine. In doing this, you are effectively completely disabling the "pmatch" function, so the motion program has absolutely no idea what the starting axis position for the move is, rendering its motion calculations nonsensical.
Reply
#15
(04-24-2011, 09:19 PM)curtwilson Wrote: John:

If there is a forward kinematic routine for a coordinate system, Power PMAC will automatically use it for the position matching (pmatch) functionality that computes the starting axis position(s) from the motor positions. This is true even if the motors are assigned to axes with axis definition statements instead of being declared as inverse kinematic axes.

By setting the "KinAxisUsed" variable (D0) to 0, you are telling Power PMAC not to pick up any axis positions from the routine. In doing this, you are effectively completely disabling the "pmatch" function, so the motion program has absolutely no idea what the starting axis position for the move is, rendering its motion calculations nonsensical.

Thanks Curt,

So, if I have a forward kinematic routine in a CS I must solve for all (relevant) axes and I must also set the appropriate axis bit in the “KinAxisUsed” (D0 ) variable.

I must be missing something, because I don’t see why the “KinAxisUsed” var is relevant. PPMAC is assuming that forward kinematics for all axes are to be handled within the kinematic routine, if one exists, regardless of how they are defined.

This does explain my strange programmed profile that I see.

John
Reply
#16
John:

The forward kinematic routine is really useful only when at least some motors in the coordinate system are defined as inverse kinematic axes (#x->I). Otherwise, Power PMAC can just mathematically invert the axis-definition equations.

With inverse kinematic equations, Power PMAC has no automatic way of knowing which axes are being used. This is what the "KinAxisUsed" (D0) variable is for.
Reply
#17
(04-25-2011, 09:19 AM)curtwilson Wrote: John:

The forward kinematic routine is really useful only when at least some motors in the coordinate system are defined as inverse kinematic axes (#x->I). Otherwise, Power PMAC can just mathematically invert the axis-definition equations.

With inverse kinematic equations, Power PMAC has no automatic way of knowing which axes are being used. This is what the "KinAxisUsed" (D0) variable is for.

After Setting "KinAxisUsed" (D0) correctly, the motion profile is working as expected.