Jump to content
OMRON Forums

Modbus TCPIP communication with UMAC


guoke1225

Recommended Posts

I build up Modbus TCPIP communication with UMAC successfully, for the coil and discrete read/write , it is worked normally. and for the registers read/write, it seems that only 16-bit registers can worked normally. because of bit 16 to 23 for X:memory and Y:memory are not used, if I define a register which bits is larger than 23 bits, the data received is wrong. and if I define a register which is a float type value, It can't receive data.

M2040->L:$107A4 //pointer to 48 bits value.

M2041->F:$107A5 //pointer to float type value.

 

so is there any solutions to avoid this issue? read/write values which bits is larger than 23 bits, and read/write float values correctly.

Link to comment
Share on other sites

  • 2 months later...
  • Replies 1
  • Created
  • Last Reply

Top Posters In This Topic

Top Posters In This Topic

Hopefully this is better late than never.

 

Using 2 UMACs, one as client and one as server, I am able to receive float data that is sent in IEEE 32 bit float format. For instance, 00111111100000010100011110101110 is roughly 1.01. I broke that into two Modbus registers and converted into decimal:

0011111110000001 = 16527

0100011110101110 = 18350

M1->X:$10780,16

M2->Y:$10780,16

M1 = 16527

M2 = 18350

I set up Modbus with FC16, Modbus Ref#0, PMAC Ref#0, Count length 2.

 

Then, on the Server:

M1->F:$10780

M1=1.0099999905

 

PMAC reads in using big endian format, so maybe you need to either convert to big endian or rearrange the byte assignments in PMAC.