How to monitor the Safe Torque Off in Power Brick LV
#1
The BrickAC.STO 0/1 can be used in Brick AC controller to monitor the Safe Torque Off status, does these BrickAC.STO 0/1 commands can be used in Power Brick LV also?
Reply
#2
The Power Brick LV does not exhibit an amplifier fault in the motor status when the STO is triggered, it is strongly advised to issue a kill to all active motors as soon as the STO is triggered. This can be done in a background PLC. It is suggested to wire the STO feedback to input#1 of the Power Brick LV.

See the "STO" section of the "Power Brick LV User Manual" for implementation details.
Reply