So we're setting up a machine to use a Power Brick with a Siemens PLC. We have the 72EX card installed, but I can't figure out for the life of me how to set it up for Profinet! I've read the manual, and it just looks like handwaving unless you're setting up ENIP.
I was encouraged to read about a "ACC-72EX Setup Assistant Software", but was unable to locate it, and I can't tell if that would even be of use to me.
Has anyone here set one up for Profinet, or does anyone know what that would look like? Thanks everyone!
Posts: 80
Threads: 16
Joined: Dec 2010
04-05-2018, 11:51 PM
(This post was last modified: 04-05-2018, 11:56 PM by tecnico.)
I use it with another bus (cclink) but basically the ACC72EX is a "carrier" for a Hilscher communication module and interfaces the PPMAC to the module's DPRAM
On the manual is a ACC72EX init PLC and date exchange script PLCs, but you still have to program the Hischer ComX with Sycon.net AFAIK
Posts: 4
Threads: 2
Joined: Jul 2016
(04-05-2018, 11:51 PM)tecnico Wrote: I use it with another bus (cclink) but basically the ACC72EX is a "carrier" for a Hilscher communication module and interfaces the PPMAC to the module's DPRAM
On the manual is a ACC72EX init PLC and date exchange script PLCs, but you still have to program the Hischer ComX with Sycon.net AFAIK
So I've got the Sycon.net open, and I don't see any reference to an ACC-72EX device.
How did you get that talking?
Posts: 80
Threads: 16
Joined: Dec 2010
Sycon doesn't talk to ACC72Ex but only to the module mounted on the ACC72Ex (Hilscher COM-C or COM-X) vua the micro usb port in the front panel of the ACC72EX.
On the PMAC side there is a example PLC in the manual that enables data communication between the module and the host system (PMAC)