dholden Posted March 8, 2018 Share Posted March 8, 2018 In the Turbo PMAC the On-Line command for open loop mode was #1o0 for zero torque #1o50 for 50% torque #1o100 for 100% torque in a PLC the code would be cmd"#1o50" What is the command(s) for open loop mode in PPMAC (on-Line and in a PLC)? Also the max allowable torque was at register Ixx69, Output Command Limit/Scale, (0-32,767). What is the PPMAC equivalent? In the Turbo and you were in open loop mode you could changed the open loop magnitude via suggested M-Var xx79 (a value of 0-32,767 resulted in 0-100% torque). How is this accomplished in the PPMAC? Finally, what is the best variable to monitor if you are in open loop mode, int he Turbo it was suggested M-Var Mxx38? Link to comment Share on other sites More sharing options...
Eric Hotchkiss Posted March 9, 2018 Share Posted March 9, 2018 For the online command, all you have to do is type the whole word "out" #1out50 The in program version of the command would be: Cout 1:50 see page 1238 of the October 2017 Software Reference Manual: You can still use command quotes: cmd "#1out50" Max allowable torque is in Motor[x].MaxDac, which can still be addressed as ixx69 just like most other legacy I-Variables. I'm not sure which variable you are looking for with Ixx79. For a brushed motor, you would bias the DAC output with Motor[x].DacBias. For a brushless motor, you would bias the ADCs with Motor[x].IaBias and Motor[x].IbBias. Motor[x].IbBias is the one that translates directly to Ixx79. For open loop, it looks like we traded that status bit for the closed loop status bit: Motor[x].ClosedLoop For motor status bits in general, open up the status window, click the motor tab, choose the status bit you need and put Motor[x]. in front. I have a feeling you will also find addressing multiple motors helpful: #1..4J+ #1,3,7J- #1,3..5,10J:10 Link to comment Share on other sites More sharing options...
Recommended Posts