Hello everyone:

 

I'm using a turbo PMAC2 CPU, and I have a serial devices need to interface with the delta tau(receive some HEX data from PMAC).

 

The problem happened as follow:

 

I'm trying to a set of HEX numbers like "00 01 02 03 04 05 06 07 08 09 0A 0B 0C 0D"(14 numbers in total),all these values are assigned to the M-variables from M0-M13, the PLC program are listed blow.

 

--------Begining of the program-------

CLOSE

 

I52=5 ;Basic setup to enable auxiliary serialport

I53=15 ;Baud rate is set to 115200

I1 = 1

I43 = 3

 

M100->X:$FFFFE1,24 ;The number of bytes to output

M101->X:$FFFFE3,24 ;Starting address to send

M102->X:$FFFFE0,23 ;bit 23 of X:$FFFFE0 must be set to 1 to enable the output

 

M0->Y:$3600,0,8

M1->Y:$3601,0,8

M2->Y:$3602,0,8

M3->Y:$3603,0,8

M4->Y:$3604,0,8

M5->Y:$3605,0,8

M6->Y:$3606,0,8

M7->Y:$3607,0,8

M8->Y:$3608,0,8

M9->Y:$3609,0,8

M10->Y:$3610,0,8

M11->Y:$3611,0,8

M12->Y:$3612,0,8

M13->Y:$3613,0,8

 

OPEN PLC1 CLEAR

M0=$00

M1=$01

M2=$02

M3=$03

M4=$04

M5=$05

M6=$06

M7=$07

M8=$08

M9=$09

M10=$0A

M11=$0B

M12=$0C

M13=$0D

 

M101=$3600

M100=13

M102=1

DISABLE PLC 1

CLOSE"

------End of the program---------

 

But I received a string "00 01 02 03 04 05 06 07 08 09 00 00 00 00", then, I changed the value of "M100" to "19", and I received a string "00 01 02 03 04 05 06 07 08 09 00 00 00 00 00 0A 0B 0C 0D 00", I'm curious about this output, why does five 0 Byte appear? anyone could tell me what happened? Thanks a lot!

Link to comment
Share on other sites

  • Replies 3
  • Created
  • Last Reply

Top Posters In This Topic

Top Posters In This Topic

--- you are not assigning the Mvar registers in order as you think... there are 5 extra registers in the middle... change you addressing so they are all in sequence

 

M0->Y:$3600,0,8

M1->Y:$3601,0,8

M2->Y:$3602,0,8

M3->Y:$3603,0,8

M4->Y:$3604,0,8

M5->Y:$3605,0,8

M6->Y:$3606,0,8

M7->Y:$3607,0,8

M8->Y:$3608,0,8

M9->Y:$3609,0,8

 

.... here are the 5 0 bytes... they are between 3609 and 3610

 

Y:$360A

Y:$360B

Y:$360C

Y:$360D

Y:$360E

 

M10->Y:$3610,0,8 change this to 360A

M11->Y:$3611,0,8 change this to 360B

M12->Y:$3612,0,8 change this to 360C

M13->Y:$3613,0,8 change this to 360D

Link to comment
Share on other sites

--- you are not assigning the Mvar registers in order as you think... there are 5 extra registers in the middle... change you addressing so they are all in sequence

 

M0->Y:$3600,0,8

M1->Y:$3601,0,8

M2->Y:$3602,0,8

M3->Y:$3603,0,8

M4->Y:$3604,0,8

M5->Y:$3605,0,8

M6->Y:$3606,0,8

M7->Y:$3607,0,8

M8->Y:$3608,0,8

M9->Y:$3609,0,8

 

.... here are the 5 0 bytes... they are between 3609 and 3610

 

Y:$360A

Y:$360B

Y:$360C

Y:$360D

Y:$360E

 

M10->Y:$3610,0,8 change this to 360A

M11->Y:$3611,0,8 change this to 360B

M12->Y:$3612,0,8 change this to 360C

M13->Y:$3613,0,8 change this to 360D

Oops!I have made the elementary mistake, the address is a HEX number. thanks a lot, @Unit101! You have done me a great favor.

Link to comment
Share on other sites

--- you are not assigning the Mvar registers in order as you think... there are 5 extra registers in the middle... change you addressing so they are all in sequence

 

M0->Y:$3600,0,8

M1->Y:$3601,0,8

M2->Y:$3602,0,8

M3->Y:$3603,0,8

M4->Y:$3604,0,8

M5->Y:$3605,0,8

M6->Y:$3606,0,8

M7->Y:$3607,0,8

M8->Y:$3608,0,8

M9->Y:$3609,0,8

 

.... here are the 5 0 bytes... they are between 3609 and 3610

 

Y:$360A

Y:$360B

Y:$360C

Y:$360D

Y:$360E

 

M10->Y:$3610,0,8 change this to 360A

M11->Y:$3611,0,8 change this to 360B

M12->Y:$3612,0,8 change this to 360C

M13->Y:$3613,0,8 change this to 360D

Hello Unit101, sorry to disturb you again, I'd like to know whether PMAC send bytes one by one to serial port, or all bytes at one shot. Thanks for your time!