Hello Everyone,

 

I have 4 axes clipper controller with op-12 ,i configure 5 axis and its working fine.

But i faced problem during homing in handwheel port only A,/A,B,/B singnals are available C,/C (index pulse) missing .

 

I have to home this axis on home switch + index pulse........

 

Is their any solution for this........

or other any way to home this axis on home switch + index pulse.....

 

..

Link to comment
Share on other sites

  • Replies 9
  • Created
  • Last Reply

Top Posters In This Topic

Hello Everyone,

 

I have 4 axes clipper controller with op-12 ,i configure 5 axis and its working fine.

But i faced problem during homing in handwheel port only A,/A,B,/B singnals are available C,/C (index pulse) missing .

 

I have to home this axis on home switch + index pulse........

 

Is their any solution for this........

or other any way to home this axis on home switch + index pulse.....

 

..

Link to comment
Share on other sites

Hello Ashish,

 

I think that the best idea that I have is to wire the index signal into the User Flag input on J9. This approach would require two home moves. First, home to the Home Flag. Second, change I6812 and I6813 for using the User Flag, and home again.

Link to comment
Share on other sites

Hello Ashish,

 

I think that the best idea that I have is to wire the index signal into the User Flag input on J9. This approach would require two home moves. First, home to the Home Flag. Second, change I6812 and I6813 for using the User Flag, and home again.

Link to comment
Share on other sites

Note that the Handwheel encoder index for the first channel (C-channel HWC1) is located on the JTHW port bit zero (DAT0 pin 3 of J8). A power on PLC will be required to set the JTHW Port Data Type Control Register bit zero to a value of zero to change it from the standard JTHW function to the alternate HWC1 function – all other features of this port can be left at their default settings.

From the Turbo SRM:

Y:$078406 JTHW Port Data Type Control Register

Bits: 0 DAT0 Data Type Control (0=HWC1; 1 =DAT0)

 

Use the following startup PLC:

 

M42->Y:$78406,0,24 ; J8 port data type control (1 = I/O; 0 = flag function)

 

//Power-up PLC:

Open plc 1 clear

M42 = $FFFE ; bit 0 flag function all others standard

Disable plc 1

Close

 

If needed the JTHW inversion control may be found at: X:$078406

Link to comment
Share on other sites

Note that the Handwheel encoder index for the first channel (C-channel HWC1) is located on the JTHW port bit zero (DAT0 pin 3 of J8). A power on PLC will be required to set the JTHW Port Data Type Control Register bit zero to a value of zero to change it from the standard JTHW function to the alternate HWC1 function – all other features of this port can be left at their default settings.

From the Turbo SRM:

Y:$078406 JTHW Port Data Type Control Register

Bits: 0 DAT0 Data Type Control (0=HWC1; 1 =DAT0)

 

Use the following startup PLC:

 

M42->Y:$78406,0,24 ; J8 port data type control (1 = I/O; 0 = flag function)

 

//Power-up PLC:

Open plc 1 clear

M42 = $FFFE ; bit 0 flag function all others standard

Disable plc 1

Close

 

If needed the JTHW inversion control may be found at: X:$078406