Program rewind
#1
NCpro 5.2 running on Win7.

Everything seems to work but the program rewind button.
Is this button handled through a PLC or is it handled from within the
front end Nc program?
If it is handled through a plc, which one, were?
Can program rewind be activated from a plc if I want to have some
event cause a rewind?

Mark
Reply
#2
(01-22-2014, 03:13 PM)kramrellim Wrote: NCpro 5.2 running on Win7.

Everything seems to work but the program rewind button.
Is this button handled through a PLC or is it handled from within the
front end Nc program?
If it is handled through a plc, which one, were?
Can program rewind be activated from a plc if I want to have some
event cause a rewind?

Mark

This is handled in the Reset PLC. The rewind section is towards the end.
Reply
#3
The button sets P988 (REWIND_INIT) the Reset.plc monitors this and performs the following action:
@SET_ON(CS_COMMAND3_M,CS_PRG_REWIND).
Reply