On a PowerBrick-LV, (Firmware 1.6.1.1, IDE 1.7.0.44) configured as Macro-auxliary,

we have declared a brushless motor as slave Node 0, drived in PWM over MACRO (by a rack Power-UMAC).

We activated the motor as Macro-slave by :

Motor[1].pMotorNode = PowerBrick[0].MacroInA[0][0].a

Motor[1].MotorNodeOffset = 64

Motor[1].MotorMode = 5 // PWM by MACRO

 

Problem on the PowerBrick:

The Motor phase measured current "Motor[1].IaMeas, .IbMeas" are not copied in PowerBrick[0].MacroOutA[0][1] and [2]

(instead, there is a bad value depending of the encoder position ??, same value is in .MacroOutA[0][1] and .MacroOutA[0][2], but shifted of 16bits left in .MacroOutA[0][1] !)

Ps: the values written in PowerBrick[0].MacroOutA[0][0] (encoder pos) and PowerBrick[0].MacroOutA[0][3] (Status & Flags) are full ok

 

Have we missing something ?,

or is there a real problem and what is the way to turn around it ?

 

PS: with Motor[1].MotorMode =0 (Local contol) the motor works ok.

 

Thanks for your Help,

S.Brun

Link to comment
Share on other sites

  • Replies 7
  • Created
  • Last Reply

Top Posters In This Topic

Hello Brad,

Thank you,

Here-under my parameters and find attached the global pp_save.cfg.

 

// ++ Clocks ++

Sys.WpKey=$AAAAAAAA;

PowerBrick[0].PhaseServoDir = 0 //Master

PowerBrick[0].PhaseFreq = 32000 //Phase-Clock =32 KHz (=freq du Ring)

PowerBrick[0].PhaseClockDiv = 0

PowerBrick[0].ServoClockDiv = 3 //Servo-Clock = 8 KHz

PowerBrick[0].PhaseClockMult= 0;

PowerBrick[1].PhaseServoDir = 3 //pas Master

PowerBrick[1].PhaseFreq = 32000 //Phase-Clock =32 KHz (=freq du ring)

PowerBrick[1].PhaseClockDiv = 0

PowerBrick[1].ServoClockDiv = 3 //Servo-Clock = 8 KHz

PowerBrick[1].PhaseClockMult= 0;

Sys.PhaseCycleExt = 1 //(i7) <- division par 2 de la Freq-Phase car MACRO (=16K)

Sys.RtIntPeriod = 2 //(i8) Période du Rti

Sys.ServoPeriod = (PowerBrick[0].ServoClockDiv +1)/PowerBrick[0].PhaseFreq //(i10) (en msec)

Sys.PhaseOverServoPeriod =1/(PowerBrick[0].ServoClockDiv +1); //(utilisé uniquement si servo à la Phase-rate)

// Macro

PowerBrick[0].MacroModeA =$00408000; //->Ce Master est: Slave, synch par le Ring (= idem un Gate2 *256)

PowerBrick[0].MacroModeB =$0; //->Ce Master est: non actif

PowerBrick[0].MacroEnableA =$0F803F00; //Master-n°0: Nodes 0,1,2,3,4,5 validés (= idem un Gate2 *256)

PowerBrick[0].MacroEnableB =$0; //Master-n°1: -aucun node validés-

Macro.TestPeriod = 20; // macro ring cycles in test period (i80)

Macro.TestMaxErrors = 2; // max macro errors allowed in test period (i81)

Macro.TestReqdSynchs = 16; // min synch packets needed in test period (i82)

// Motors

Motor[1].pMotorNode = PowerBrick[0].MacroInA[0][0].a //Consignes sur: Gate3-0, ICMacro-A, Node-0

Motor[1].MotorNodeOffset = 64 //=64 si Gate3, =0 si Gate2)

Motor[1].MotorMode = 5 //=5 PWM par MACRO

 

Motor[1].ServoCtrl = 1 // L'axe doit etre actif sur le Slave

Motor[1].PhaseCtrl = 4 //(=1 Gate3 ou =4 Gate1 ou pas packed) même si commandé MACRO en PWM (.MotorMode= 5)

Motor[1].pEncCtrl = PowerBrick[0].Chan[0].OutCtrl.a //(Control Ampli)

Motor[1].pDac = PowerBrick[0].Chan[0].Pwm[0].a //(si .MotorMode= 5) Consignes lue sur MACRO

Motor[1].pEncStatus = PowerBrick[0].Chan[0].Status.a // (Status Ampli)

Motor[1].pAmpEnable = PowerBrick[0].Chan[0].OutCtrl.a //(Enable Ampli)

Motor[1].pAmpFault = PowerBrick[0].Chan[0].Status.a // (Fault Ampli)

Motor[1].pLimits = PowerBrick[0].Chan[0].Status.a // Limites

Motor[1].pAdc = PowerBrick[0].Chan[0].AdcAmp[0].a //(si .MotorMode= 5) Courants émis sur MACRO

Motor[1].pEnc = EncTable[1].a //(si .MotorMode= 5) Feedback émis sur MACRO

Motor[1].pEnc2 = EncTable[1].a // ici peu importe la .pEnc car aucun codeur connecté PowerBrick

Motor[1].AmpFaultLevel =1

Motor[1].EncType =5

 

Gate3[0].Chan[0].PackOutData = 0 //Pour PowerBrick-LV (1=defaut)

Gate3[0].Chan[0].PackInData = 0 //Pour PowerBrick-LV (2=defaut)

pp_save.cfg.txt

Link to comment
Share on other sites

I have only tested the Power Brick auxiliary feature in Torque mode. The majority of people use it this way. Any particular reason why you want to do PWM instead? There is no benefit in further loading the master, especially that the slave unit possesses a CPU which might as well be put to use (computational load sharing). So that eventually the commutation and current loop are performed locally at the slave side.

 

Nevertheless, the current feedback should come back properly... I can take a look at this when I get back into the office sometime next week.

Link to comment
Share on other sites

I di not see anything you have missed. I do not have a system to test with so the best option seems to be to do as Richard suggests and unload the main CPU by letting the slave do some of this work. That will get you going and later Richard can see why your setup did not work.
Link to comment
Share on other sites

Thank you Brad and Richard,

You're absolutely right, and the final projet will be composed with several PowerBrick with SinCos-ACI option drived in Torque mode.

 

For the moment, and quickly, we have to validate the process of the machine.

For that, we have to drive a linear motor with a sincos encoder and our PowerBrick has not the option Sincos installed. We have only a Power-UMAC with Macro and Acc24E3 available to read the SinCos.

It's why we try to work with the PowerBrick in Macro-PWM mode.