help to setup a modbus Geobrick - eobe - 07-30-2014

Hello, I need help to setup a modbus Geobrick.
The Geobrick (master) communicates with a safety PLC (slave)

The Modbus protocol says to communicate, you must configure (on the master ) the IP address, the slave number and the register number + function code (3 for Read Holding Registers or 16 for Write Multiple Registers)

At PEWIN32, I do not see how to configure the slave number and register number. Can someone explain me?
I see, you need to configure the "Modbus reference #", but what data should I put (N° slave + starting adresss?? Unit identifier ?)?

[attachment=830]
When I use a program like "Modbus Doctor", I can read the desired value (see screenshot below).

[attachment=831]

thank you in advance for your help


RE: help to setup a modbus Geobrick - steve.milici - 08-07-2014

There is a description of how this is computed in the Pewin32 Pro2 Software Manual in the section "Modbus Setup Window" on page 44:
http://www.deltatau.com/manuals/pdfs/PEWIN%2032%20PRO%202%20SOFTWARE.pdf?id=635415374142578227

Also see the documents at our FTP-site:
http://ftp.support.deltatau.com/DT-USA/Training%20Documents/Modbus/