The BrickAC.STO 0/1 can be used in Brick AC controller to monitor the Safe Torque Off status, does these BrickAC.STO 0/1 commands can be used in Power Brick LV also?
The Power Brick LV does not exhibit an amplifier fault in the motor status when the STO is triggered, it is strongly advised to issue a kill to all active motors as soon as the STO is triggered. This can be done in a background PLC. It is suggested to wire the STO feedback to input#1 of the Power Brick LV.

See the "STO" section of the "Power Brick LV User Manual" for implementation details.